Actually, I wonder if there's any good use for AC/h. Can't think of one off the top of my head but maybe I'm being dozy.
of course your milage may vary, but in our case the building regs minimums were in reality over specified..
Seems to recommend 0.3 ACH
Just trying to understand.
Uncessary air flow, via MVHR, is a waste of energy. In my case the MVHR was under specified anyway, I am lucky that it seems to be enough and I can avoid running at flat chaff all the time. Triassic, I get your unhappiness with MVHR sales men, procrement was a right pain, but do take care not to end up with a fan that is too small for the volume of your house. It is nice to know you can ramp it up if you need too even if daily rate is gentle.
As a unit ACH is useful to give a clear view on how long will it take to totally replace the (smelly/humid) air with new. Of particular interest when evacuating a polutant, but less informative when continuously ventilating, and I have been unable to find an explanation why 0.3ACH is a good level. In a tiny room full of bodies this would be insufficient, in a vast empty room sucking cubic meters out every hour would be unncessary and drafty.
It seems to me that the amount of air movement you need depends on how much smell, CO2 or humidity you are generating. That would best be specified as a flow rate (l/s) but related to number of occupants or pollutant generation rate. A shower in a small bathroom creates the same rate of steam as one in a large bathroom.
Also just because I have MVHR (replacing random losses depending on wind and building air pearmeability), does not mean that I no longer want to clear the steamy bathroom in a reasonable time. I want a boost level necessary and sufficient for the volume of the bathroom, not just a set l/s regardless of the room size.
Finally I think I calcualted at some time that 0.3l/s per sqm floor area is around 0.3 ACH for the average hight of room. So I guess that I where the number comes from.
I am running mine well below the calculated rates - do not even boost for showers and they still clear quite quickly. I have a CO2 sensor from our old friend JSH but I have just not had the time to set it up and see what the values are.
In reality, despite the expense, I'd drive my system by CO2 levels if I did it again.
A MVHR unit can only move so much air for a given static pressure provided by the ducting connected to it and the room vents. I expect that the suppliers are looking at the volume of air in your house, including the vaulted rooms, and the length of ducting needed to reach each room and concluding that one unit is not sufficient to move that much air at the flow rates required. Be glad they are doing this, otherwise you would end up with an under powered noisey system.
http://www.gov.scot/resource/buildingstandards/2013Domestic/chunks/ch04s15.html [¹] OK, so I extended the section number a bit. :tongue:
The Part F whole house 0.3 l/s requirement equates to 0.45 air changes per hour for a dwelling with a standard 2.4 m high ceiling.
For a 100 m2 house, the 0.3 l/s rate gives 100 x 0.3 = 30 l/s or 108 m3/hr
House Volume = 100 x 2.4 = 240 m3
AC rate = 108/240 = 0.45 AC / hr.
Paul in Montreal.
More seriously the minimum ventialtion of habitable rooms of around 0.5ACH seems to be an international standard. See http://www.aivc.org/sites/default/files/members_area/medias/pdf/Conf/2004/2004028_Yoshino.pdf. There was a graph in another thread, but can't see it at the moment. But I have not been able to find any research that establishes *why* such a rate is needed. Has it ever been justified?
The rules were expressed in different ways but for a model house came out as around 0.5ACH in most places. What research justifies this rate, or is it just tradition?
They are opposite ends of the ventilation 'equation'...:smile:
Let's stick to ventilation.
From that survey of ventilation requirements it would seem that most countries demand we ventilate our houses more than I, and several others, currently are. Many nations base the requirement on floor area or ACH, which I believe model the amount of smells/pollution/humidity generated very poorly - think one person in a large house with high ceilings. This means if we comply then we are either wasting energy through vents, or wasting (less) energy running MVHR fans. Even if we turn the fan down we stil have to buy powerful enough units (sometimes multiple) in the first place with the embodied energy that entails. My guess is that the various bodies have just copied standards from each other, I can't find any supporting research.
It seems to me that the world needs some research on how much ventiation we really need, based on occupants and activities, measurements of CO2, formaldehyde etc. , not arbitrary floor area etc. and over cautious rules of thumb.
Paul in Montreal.
However, your comment which I thought was a joke was mixing up very different things. Firstly, I think it mixes up a discussion of the minimum ventilation required for health under any conditions with the maximum allowed under windy conditions (represented by +/- 50 pascals internal pressure) for energy conservation reasons.
Secondly, it seems to mix up the way in which incidental leakage tends to scale with pressure (which itself depends on the geometry of the leaks) with the way an MHRV system will react to pressure and wind. Basically, if you pressurize the house it doesn't make the fans blow harder so you wouldn't expect the flow through an MHRV to react in anything like the same way.
So, if your comment wasn't facetious/a joke then perhaps you could explain it a bit more fully because I don't get what you're saying.