Terry, what is the nature of your rubble fill?
U-values recognise neither of these.
1.The conductivity [k-value] and respective surface areas/ volumes of the irregular fill and any air pockets would need to be estimated in the same way that thermal bridging of wall ties is now allowed for in BR443. A complicated calculation if you are not familiar with this kind of thing and in my view not worth the effort. Better to try and agree something with your BCO
2. Air infiltration losses are not taken into consideration so the more airflow you have the less reliable any predictions are going to be.
You may get away with a simplified calculation assuming the wall is all made from a worst case conductivity [ie slate] That is the approach I would take BUT air losses are still not accounted for.
Tom, in a very old house (at the moment).
tom
Frank
As for u-values, there is no recognised/accepted value for rubble stone that I have been able to discover over more than two years of arguing with BCOs. Given that a quarter of our housing stock is pre-1914, and a significant proportion of that has solid walls, there's a real need for some research into this area. Current BCO thinking would seem to be to demand multifoil and drylining at the very least, and few seem to have heard of lime/hemp insulation, so heaven help anyone in an old house who wants to preserve interior detailing.
A project that got cancelled, previous owner seemed to have injected rubble walls with urethane foam somehow - great nibs of it had exuded from many joints, where unfinished in hidden area. I dreaded to think what that might have done to wall longevity and water resistance, hence my interest in injection with lime mortar, above. If lime mortar, how about hemcrete?
It's fiddly work and expensive, unfortunately. Particularly since vast quantities of grout can be needed, and then you find out that it's found the line of least resistance and filled up an old sump or cess-pit near the wall! However it can save a building - large parts of York Minster are standing today thanks to grouting.
It's also far greener than using polymer foam - and it still allows for breathability and autogenic fracture healing.
On a smaller scale it can be done - but not as well- with a pointing gun to fill lesser voids and cracks in domestic rubble-stone walls.
Yep, sounds good. No water penetration problems? - accidental long distance void/passages created, as is the old danger with cavity retrofill?
tom
That will give an instant surface temperature at that spot . Take the temperature on both sides of the wall, you know the wall area, the time 'is' one second, so the energy needed to maintain that wall temperature can be calculated. Of course the readings should be at regular intervals over 24 but then you would need an expensive thermocouple and data logger. The beauty of taking spot temperatures is that you can see the direction of heat flow, similar to a thermal picture but limited to a much smaller area. Simple, fast, rough and ready but saves having to consider the wall structure.
As an interesting mind-experiment, what you're suggesting in fact shows up the whole obsolete myth of U-value thinking - which ignores the overwhelming effects of both thermal massiveness, and of the non-steady-state that is real life. Which is why conventional insulants give actual heat retention results, over a period, as poor as 40% of what plain U-value calcs would expect; and why old solid buildings with pathetic calc's U-values often perform well; and why multifoil insulation works so well, because it understands and exploits the non-steady-state.
I should have mentioned that there should be a steady temperature state, that was assumed. There should be spot temps taken over the wall giving a thermal pictuure, not as bright and complete as that of a thermal camera but the infra-red thermometer remains well within the financial range of most of us.
tom